Power Factor Correction MCQs

Practice Power Factor Correction MCQs with four options, answers and explanations for focused Electronics & Telecommunication Engineering revision.

Question 1
Network TheoryPower Factor Correction

A 1 kW load operates at 0.8 lagging power factor. The reactive power is approximately 0.75 kVAR. To correct the power factor ideally to unity, the shunt capacitor bank should supply approximately?

  • A0.25 kVAR leading
  • B0.5 kVAR leading
  • C0.75 kVAR leading
  • D1.25 kVAR leading
Report an error
Correct Answer: C. 0.75 kVAR leading
Explanation: Unity power factor requires cancellation of the load's lagging reactive power, so the capacitor should provide about 0.75 kVAR leading.
Reference: Standard network theory: reactive compensation
Question 2
Network TheoryPower Factor Correction

Improving a lagging load power factor by connecting a shunt capacitor primarily reduces the source?

  • AReactive current component
  • BReal power demanded by the load to zero
  • CSupply frequency
  • DLoad resistance to zero
Report an error
Correct Answer: A. Reactive current component
Explanation: The capacitor supplies leading reactive current locally, reducing the lagging reactive current drawn from the source while the load real-power requirement is essentially unchanged.
Reference: Standard network theory: power factor correction